Hey Won,

> One thing left is how i can into the SEL. I tried this with other tools. None 
> of them gave an output. :(

Do you mean you can't access the SEL in multiple IPMI software?

Can you send me the --debug output from running ipmi-sel?  Let's see what the 
problem is.

Al

On Fri, 2009-04-03 at 11:57 -0700, Won De Erick wrote:
> --- On Fri, 4/3/09, Al Chu <address@hidden> wrote:
> > Hey Won,
> > 
> > The reason for what you're seeing is described in the
> > ipmimonitoring
> > manpage.
> > 
> > ---
> > Interpretation rules have not been written for all sensors
> > permutations
> > and types. Users may notice some sensors output in
> > ipmi-sensors(8) do
> > not output in ipmimonitoring. If sensor interpretation
> > rules are needed,
> > please contact the FreeIPMI maintainers.  
> > ---
> > 
> > Looking at your sensors output below, there are three OEM
> > sensors that I
> > can't interpret b/c I don't know the interpretation rules
> > for them.  The
> > Power Unit Device Install and Fan transition
> > interpretations were
> > recently added in 0.7.3.  So if you update to atleast
> > 0.7.3, those
> > readings should show up in ipmimonitoring.
> > 
> > As for why Temperature Sensors aren't showing up, this
> > corner case for
> > HP machines also appears to have been fixed in 0.7..3.
> 
> Thank you for the tip. I installed the latest, 0.7.6, instead. 
> 
> hpdl380-fbsd71r# ipmi-sensors
> 1: UID Light (OEM Reserved): [OEM State = 0000h]
> 2: Int. Health LED (OEM Reserved): [OEM State = 0000h]
> 3: Ext. Health LED (OEM Reserved): [OEM State = 0000h]
> 4: Power Supply 1 (Power Supply): [Presence detected]
> 5: Power Supply 2 (Power Supply): [NA]
> 6: Power Supplies (Power Supply): [Non-redundant:Sufficient Resources from 
> Redun                      dant]
> 8: VRM 1 (Power Unit): [Device Inserted/Device Present]
> 9: VRM 2 (Power Unit): [Device Inserted/Device Present]
> 10: Fan 1 (Fan): [transition to Running]
> 11: Fan 2 (Fan): [transition to Running]
> 12: Fan 3 (Fan): [transition to Running]
> 13: Fan 4 (Fan): [transition to Running]
> 14: Fan 5 (Fan): [transition to Running]
> 15: Fan 6 (Fan): [transition to Running]
> 16: Fans (Fan): [Fully Redundant]
> 18: Temp 1 (Temperature): 35.00 C (NA/70.00): [OK]
> 19: Temp 2 (Temperature): 17.00 C (NA/39.00): [OK]
> 20: Temp 3 (Temperature): 30.00 C (NA/127.00): [OK]
> 21: Temp 4 (Temperature): 30.00 C (NA/127.00): [OK]
> 22: Temp 5 (Temperature): 46.00 C (NA/77.00): [OK]
> 23: Temp 6 (Temperature): 30.00 C (NA/127.00): [OK]
> 24: Temp 7 (Temperature): 30.00 C (NA/127.00): [OK]
> 25: Power Meter (Current): [Device Enabled]
> 
> 
> hpdl380-fbsd71r# ipmimonitoring
> Record_ID | Sensor Name | Sensor Group | Monitoring Status| Sensor Units | 
> Sensor Reading
> 4 | Power Supply 1 | Power Supply | Nominal | N/A | 'Presence detected'
> 6 | Power Supplies | Power Supply | Critical | N/A | 
> 'Non-redundant:Sufficient Resources from Redu    ndant'
> 8 | VRM 1 | Power Unit | Nominal | N/A | 'Device Inserted/Device Present'
> 9 | VRM 2 | Power Unit | Nominal | N/A | 'Device Inserted/Device Present'
> 10 | Fan 1 | Fan | Nominal | N/A | 'transition to Running'
> 11 | Fan 2 | Fan | Nominal | N/A | 'transition to Running'
> 12 | Fan 3 | Fan | Nominal | N/A | 'transition to Running'
> 13 | Fan 4 | Fan | Nominal | N/A | 'transition to Running'
> 14 | Fan 5 | Fan | Nominal | N/A | 'transition to Running'
> 15 | Fan 6 | Fan | Nominal | N/A | 'transition to Running'
> 16 | Fans | Fan | Nominal | N/A | 'Fully Redundant'
> 18 | Temp 1 | Temperature | Nominal | C | 35.000000
> 19 | Temp 2 | Temperature | Nominal | C | 17.000000
> 20 | Temp 3 | Temperature | Nominal | C | 30.000000
> 21 | Temp 4 | Temperature | Nominal | C | 30.000000
> 22 | Temp 5 | Temperature | Nominal | C | 46.000000
> 23 | Temp 6 | Temperature | Nominal | C | 30.000000
> 24 | Temp 7 | Temperature | Nominal | C | 30.000000
> hpdl380-fbsd71r#
> 
> One thing left is how i can into the SEL. I tried this with other tools. None 
> of them gave an output. :(
> 
> The box is IPMI v2.0-compliant. I can see a lot of logs using iLO.
> 
> Thanks,
> 
> Won
> 
> 
> 
> 
>       
> 
-- 
Albert Chu
address@hidden
Computer Scientist
High Performance Systems Division